What is the approximate line-to-ground arcing fault value on a 480/277-volt system where the line-line-line fault current has been calculated to be 30,000 amperes?
A) 11,400
B) 22,200
C) 26,700
D) 30,000
Correct Answer:
Verified
Q10: If non-series-rated overcurrent devices (standard molded-case circuit
Q11: The NEC includes a requirement that the
Q12: The amount of short-circuit current from a
Q13: _ power systems are power systems that
Q14: A situation known as _ occurs when
Q15: A simple method of determining the available
Q16: The value of the square root of
Q17: To obtain the approximate short-circuit current values
Q19: What is the intent of NEC 110.9
Q20: When determining the f factor, N represents