Assume an open in the field wiring is suspected between the output module and output load device. This condition would be confirmed if:
A) full output voltage was measured at the module and 0 voltage at the load.
B) full output voltage was measured at the load and 0 voltage at the module.
C) the output status indicator on the module is on and the load is not operating.
D) the output status indicator on the module is off and the load is not operating.
Correct Answer:
Verified
Q63: Which of the following would not normally
Q64: If an output module fuse blows repeatedly,
Q65: Which of the choices of the troubleshooting
Q66: The input wiring or device is suspected
Q67: Which of the following is not normally
Q69: Which function of a PLC would be
Q70: The data monitor feature of a PLC
Q71: The force instructions:
A)will force data table bits
Q72: With reference to the condition illustrated, what
Q73: Editing a PLC program normally refers to:
A)replacement